Electric shower cutting out

Nissan 4x4 Owners Club Forum

Help Support Nissan 4x4 Owners Club Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

96terrano

Well-known member
Joined
Jun 27, 2010
Messages
8,022
thought id ask as ive been very pleased with the other non vehicle related questions & answers here:bow

basically, this problem has gone on over a year now, when the counsel fitted new bathrooms back in early 2011 we got new showers too, but in late 2011, it started randomly cutting out, tripping the breaker on the fuse board randomly

some times when you flick the trip switch it would come back on but other times the trip switch just fires off again, we spoke to the counsel and they actually hot glued the switch in the on position:eek::eek::doh anyways that sorted it, then about 2 months later the counsel came back and replaced the shower and trip switch, but the new shower still trips the switch if you have the temp over a certain setting, it seems to be ok now but will still trip say once every 2 months

any ideas?
 
Maybe fuse not rated to shower? but a good sparki should know what to do.
If council fitted it get them back
 
Maybe fuse not rated to shower? but a good sparki should know what to do.
If council fitted it get them back

yes, i don't even think the guys who did it were qualified, as it was bodged like with the hot glue:doh
 
It could be the water flow is to low and when you try to over heat the water, it cuts out, but sounds more like you have an electrical fault.
I wouldn't let those council tossers near my house, glueing the breaker in the on position :doh:doh
 
It could be the water flow is to low and when you try to over heat the water, it cuts out, but sounds more like you have an electrical fault.
I wouldn't let those council tossers near my house, glueing the breaker in the on position :doh:doh

no, problem is this is a council house, so there's nowt we can do, i wouldn't go about gluing breakers, i'd find the fault :rolleyes:
 
yes, i don't even think the guys who did it were qualified, as it was bodged like with the hot glue:doh

ffs I hope you still got the earth bonding in place . GLUE BREAKER :eek: sue the sods.
They have to be qualified to do operate a glue gun :doh
 
WHAT IS THE MAKE OF SHOWER ...RYAN

IS IT THE MCB THAT TRIPS OR THE RCBO ( RCD/MCB COMBIND )

DO YOU HAVE PROBLEMS WITH WATER PRESSURE :nenau
 
i disagree totally ..... of course theres something you can do about it , complain , or ask a qualified electrician to provide a report and test of your house electrics ,tell the council you have serious doubts about your safety and your house electrics ..... dont pussyfoot about
 
Bit confused here 96 as all the MCB's that I can think of cannot be held in the on position, whilst you can hold the external lever "up" the internals will still trip out, then when the lever is lowered again it clicks onto the internals again so that it can be reset, the only one that could be glued on that I can recall is the early Wylex with two push buttons, (one small to test and one large to reset) I guess the large one could be glued in? Rick
 
Last edited:
often when people upgrade their electric showers they fit a more powerful one to get more hot water, but then the cable and circuit breaker are the wrong size. You really should get on to yhe council and have it checked ASP tell them this is a safety issue, could cause a fire. Dont forget you pay the rent, or your Pa does.

regards bri
 
easier then explaining, house electrics aernt my thing !


IMAG1741_1.jpg
 
Dont like the look of were they have chopped out the plastic for the new fuses.
the whole consumer unit might not be up to it.
I WOULD NOT LET MY KIDS USE IT. if its tripping.
 
easier then explaining, house electrics aernt my thing !


View attachment 3200

The breaker that thet have fitted is an RCBO (a good thing) which is a combined MCB & RCD in one device.
The problem with this tripping is that you have to figure out if it is tripping as a result of the RCD function (typically leakage to earth) or as an MCB function which is a result of overload.
If you shower is in excess of 10Kw (check the rating plate) then after extended use the MCB may likely trip.
 
OK so it has been replaced with a B40 Hagar, but both the Hagar and the original MK MCB's will not allow you to fix them in the on position, what is the KW rating of the shower, Rick
 