Default house electrics question

I'm curious to why all radiators, matal sinks etc are earthed In my house, and they aren't connected to a 240/250v supply

Why is this
96terrano is offline   Reply With Quote
Old 12-01-2013, 00:41   #2
wildbri
Senior Member
Click here to find out how to become a paid up member
 
Join Date: Feb 2007
Location: south lakeland
Vehicle: terrano 1997 tdi
Posts: 940
Smile

the earth wires are fitted to all metal surfaces so that that they are all bonded together as one. should an electrical equipment become faulty so that the metal surfaces could become live then the bonding to earth will cause a fuse to blow or a circuit breaker to trip so disconnecting the faulty fitting or cable from the mains. to put it simply TO STOP YOU GETTING ELECTRICUTED. regards bri
wildbri is offline   Reply With Quote
Old 12-01-2013, 00:55   #3
96terrano
Senior Member
Click here to find out how to become a paid up member
 
Join Date: Jun 2010
Location: Dumfries and Galloway, Scotland
Vehicle: Nissan Terrano 2.7TD LWB
Posts: 8,024
Default

Ahh right...... I see now, cheers I was just curious as I thought the sinks radiation system wad isolated form any electrical systems within in house
96terrano is offline   Reply With Quote
Old 12-01-2013, 08:17   #4
rustic
Senior Member
Click here to find out how to become a paid up member
 
rustic's Avatar
 
Join Date: Feb 2007
Location: Staffordshire
Vehicle: Maverick Mk I 2.7 TD LWB
Posts: 7,825
Default

You will also find earth bonds between the hot and cold water taps on sinks and basins etc. but on older systems this was not done.
This is just in case that the hot water system becomes live say through an immersion heater fault and bad earth, thus giving 240 on one tap, and earth on the other.
Since most of us operate both taps at once... This could be lethal.

What really concerns me regarding plumbing, is that more and more people are using plastic pipes, and if used for modifications, could in fact insulate certain parts of the water system, thus loosing safety earths.

So think about safety when using plastic.

Your main earth in houses used to be either the metal water pipe or metal gas pipe, but since these are now often plastic, then the earth might come from the armoured cable near to the meter, or to an earth rod outside the building.

Never disconnect earths

Certainly RCD's or earth leakage trips help to prevent electrocution, however the lighting system is often not protected via RCD's so you are more at risk.
So treat with respect if working with lights especially in bathrooms and kitchens.
There are now a lot of legal issues regarding the extension and additional wiring added to domestic systems.
So seek advice before considering messing with wiring.

I have seen complete idiots replace wall sockets and light switches, and crossed over live and neutral, so it could have been worse, if they got the earth wrong.

This is made worse by the likes of Aldi and Lidl type places selling cheap metal clad switches and sockets, which the general public attempt to swap themselves.

If they get the earth wire wrong, and remember the lighting circuit may not have RCD protection, then this could leave the metal switch plate live.

Rant over for now...

Best regards,

Rustic
__________________
Ford Maverick GLX 1995 2.7TD LWB in illusion silver, 98k miles. Owned since new, for 22 years.
Best car I have ever owned.
Just wish I could drive it more.
rustic is offline   Reply With Quote
Old 12-01-2013, 10:02   #5
davenclaire
Senior Member
Click here to find out how to become a paid up member
 
Join Date: Dec 2010
Location: south east
Vehicle: terrano 2 lwb
Posts: 816
Default

also you msin central heating pump is 240v as are your syncro motors if they go short and they can then the central heating pipes will go live to, bang big time if you touch a radiator. just recently had to rebond all my pipes and fit a new ground earth
davenclaire is offline   Reply With Quote
Old 12-01-2013, 10:14   #6
rustic
Senior Member
Click here to find out how to become a paid up member
 
rustic's Avatar
 
Join Date: Feb 2007
Location: Staffordshire
Vehicle: Maverick Mk I 2.7 TD LWB
Posts: 7,825
Default

Quote:
Originally Posted by davenclaire View Post
also you msin central heating pump is 240v as are your syncro motors if they go short and they can then the central heating pipes will go live to, bang big time if you touch a radiator. just recently had to rebond all my pipes and fit a new ground earth
We are talking 4 mm2 cable too, not cheap and nasty flex.
__________________
Ford Maverick GLX 1995 2.7TD LWB in illusion silver, 98k miles. Owned since new, for 22 years.
Best car I have ever owned.
Just wish I could drive it more.
rustic is offline   Reply With Quote
Old 12-01-2013, 20:30   #7
Banshee
Moderator
 
Banshee's Avatar
 
Join Date: Jul 2012
Location: West Midlands
Vehicle: 04 2.7 SWB Terrano II Van
Posts: 13,526
Default

Am I right in thinking they are called "Extraneous Bonds", I remember when our's fell off our shower pipes and my brother was complaining that he was getting an electric shock from the plug hole, we laughed at him thinking he was making it up but when we checked it when the shower was on, we were getting an 11v reading from the plug hole!!!! lol

Fitted a new bond and bingo, no reading
Banshee is offline   Reply With Quote
Old 12-01-2013, 20:45   #8
solarman216
Off road maniac
Click here to find out how to become a paid up member
 
solarman216's Avatar
 
Join Date: Dec 2009
Location: Bexhill on Sea
Vehicle: Y60 Patrol Me, 3 ltr Mrs
Posts: 17,431
Default

Quote:
Originally Posted by rustic View Post
You will also find earth bonds between the hot and cold water taps on sinks and basins etc. but on older systems this was not done.
This is just in case that the hot water system becomes live say through an immersion heater fault and bad earth, thus giving 240 on one tap, and earth on the other.
Since most of us operate both taps at once... This could be lethal.

What really concerns me regarding plumbing, is that more and more people are using plastic pipes, and if used for modifications, could in fact insulate certain parts of the water system, thus loosing safety earths.

So think about safety when using plastic.

Your main earth in houses used to be either the metal water pipe or metal gas pipe, but since these are now often plastic, then the earth might come from the armoured cable near to the meter, or to an earth rod outside the building.

Never disconnect earths

Certainly RCD's or earth leakage trips help to prevent electrocution, however the lighting system is often not protected via RCD's so you are more at risk.
So treat with respect if working with lights especially in bathrooms and kitchens.
There are now a lot of legal issues regarding the extension and additional wiring added to domestic systems.
So seek advice before considering messing with wiring.

I have seen complete idiots replace wall sockets and light switches, and crossed over live and neutral, so it could have been worse, if they got the earth wrong.

This is made worse by the likes of Aldi and Lidl type places selling cheap metal clad switches and sockets, which the general public attempt to swap themselves.

If they get the earth wire wrong, and remember the lighting circuit may not have RCD protection, then this could leave the metal switch plate live.

Rant over for now...

Best regards,

Rustic
Well said mate specially about the introduction of plastic pipe for repairs, a little understood area, Rick
__________________
Ex banger racer now off road maniac
Lokka on the front with manual hubs
Diff lock on rear
3 inch SS straight through exhaust
Manly winch bumper with 13000 lb winch
10 spike ground anchor, with multiple straps and blocks
Super strong body cills capped with scaffold pole
20% stronger springs all round
aggressive off road tyres on wheels so just swap.
Aim to get stuck and be completely self sufficient in extraction, love getting muddy, 2ft deep is good but rare.
solarman216 is offline   Reply With Quote
Old 12-01-2013, 21:17   #9
rustic
Senior Member
Click here to find out how to become a paid up member
 
rustic's Avatar
 
Join Date: Feb 2007
Location: Staffordshire
Vehicle: Maverick Mk I 2.7 TD LWB
Posts: 7,825
Default

Quote:
Originally Posted by solarman216 View Post
Well said mate specially about the introduction of plastic pipe for repairs, a little understood area, Rick
I would like to thank 96 Terrano for starting his thread,
as I hope it will make people more aware of the issues of messing with electricity, and more especially in areas that involve water.

__________________
Ford Maverick GLX 1995 2.7TD LWB in illusion silver, 98k miles. Owned since new, for 22 years.
Best car I have ever owned.
Just wish I could drive it more.
rustic is offline   Reply With Quote
Old 12-01-2013, 22:21   #10
geoffdown
Senior Member
Click here to find out how to become a paid up member
 
Join Date: Aug 2010
Location: devon
Vehicle: terrano 2.7tdi SE+ (X)reg
Posts: 1,674
Default

but with plastic pipe the water inside will still make the circuit wont it i hate using plastic pipe in water surply and central heating a will always use copper pipe and solder it hate using the compression joints
geoffdown is offline   Reply With Quote
Old 12-01-2013, 22:27   #11
jims-terrano
Senior Member
Click here to find out how to become a paid up member
 
Join Date: Sep 2004
Location: UK
Posts: 12,965
Default

So with the introduction of plastic water pipes should there be an earth ring around the house to connect to all radiators and taps?

As far as I'm aware plastic is never used for gas lines.

I do know that the regulations that were brought in a few years ago require that the gas lines are bonded right up to the meter.
jims-terrano is offline   Reply With Quote
Old 12-01-2013, 22:41   #12
solarman216
Off road maniac
Click here to find out how to become a paid up member
 
solarman216's Avatar
 
Join Date: Dec 2009
Location: Bexhill on Sea
Vehicle: Y60 Patrol Me, 3 ltr Mrs
Posts: 17,431
Default

Quote:
Originally Posted by geoffdown View Post
but with plastic pipe the water inside will still make the circuit wont it i hate using plastic pipe in water surply and central heating a will always use copper pipe and solder it hate using the compression joints
no not good enough, the inside of a metal pipe will have a degree of debris on it so insulating the water from the pipe, and even if it was in good contact the resistance is high enough that a shock could result, I quoit an example, shower rise and fall unit screwed to the wall, problem was screw hit a cable and penetrated the live conductor this made the whole shower rise and fall unit live at 240 v, fortunately no one was hurt as it was discovered early, and most today employ plastic stand off's which reduce the risk (this one was all metal) but you can see the problem, Rick
__________________
Ex banger racer now off road maniac
Lokka on the front with manual hubs
Diff lock on rear
3 inch SS straight through exhaust
Manly winch bumper with 13000 lb winch
10 spike ground anchor, with multiple straps and blocks
Super strong body cills capped with scaffold pole
20% stronger springs all round
aggressive off road tyres on wheels so just swap.
Aim to get stuck and be completely self sufficient in extraction, love getting muddy, 2ft deep is good but rare.
solarman216 is offline   Reply With Quote
Old 12-01-2013, 22:43   #13
solarman216
Off road maniac
Click here to find out how to become a paid up member
 
solarman216's Avatar
 
Join Date: Dec 2009
Location: Bexhill on Sea
Vehicle: Y60 Patrol Me, 3 ltr Mrs
Posts: 17,431
Default

Quote:
Originally Posted by jims-terrano View Post

As far as I'm aware plastic is never used for gas lines.
plastic for gas is only allowed below ground, Rick
__________________
Ex banger racer now off road maniac
Lokka on the front with manual hubs
Diff lock on rear
3 inch SS straight through exhaust
Manly winch bumper with 13000 lb winch
10 spike ground anchor, with multiple straps and blocks
Super strong body cills capped with scaffold pole
20% stronger springs all round
aggressive off road tyres on wheels so just swap.
Aim to get stuck and be completely self sufficient in extraction, love getting muddy, 2ft deep is good but rare.
solarman216 is offline   Reply With Quote
Old 12-01-2013, 22:53   #14
jims-terrano
Senior Member
Click here to find out how to become a paid up member
 
Join Date: Sep 2004
Location: UK
Posts: 12,965
Default

Quote:
Originally Posted by solarman216 View Post
plastic for gas is only allowed below ground, Rick
Yes very true, I mean't the Hep2o grey or white pipes running water around the house.

Interesting that whilst we are on the subject of electrical safety the regs actually state "a competant person" as far as the fitter and tester is concerned. I guess competancy is someones opinion and is rather vague.
jims-terrano is offline   Reply With Quote
Old 12-01-2013, 23:00   #15
96terrano
Senior Member
Click here to find out how to become a paid up member
 
Join Date: Jun 2010
Location: Dumfries and Galloway, Scotland
Vehicle: Nissan Terrano 2.7TD LWB
Posts: 8,024
Default

Quote:
Originally Posted by rustic View Post
I would like to thank 96 Terrano for starting his thread,
as I hope it will make people more aware of the issues of messing with electricity, and more especially in areas that involve water.

It was just curiosity thought id ask here as I've seen good answers on electrical questions before...I'm not displeased with the responses
96terrano is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT +1. The time now is 18:58.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Images online photo albums