Changing domestic rcd from a 16amp to a 32amp
My stick welder blows fuses over 100 amps
No, it's got a standard 13 amp fuse domestic plug into standard socket in garage. The garage has its own board with a 100amp mcb and the sockets have a b16 16amp rcd. So I'm thinking of swapping the socket on the wall for a blue 16 amp socket with same 16 amp plug on welder. Can I swap the rcd easily enough for a larger 32 amp one So I can crank those Amps well past my current 100 amp limit ?? |
25-10-2012, 17:08 | #2 |
Senior Member
Join Date: Feb 2012
Location: Staffs
Vehicle: '02 Terrano TDI sport lwb
Posts: 3,787
|
That last but should say 13amp limit, not 100amp
|
25-10-2012, 18:16 | #3 |
Senior Member
Join Date: Apr 2008
Location: on the beach WEST WALES
Vehicle: Maverick TDi BLACK mmm
Posts: 15,136
|
The RCD you're replacing is there to protect the existing cable size. Is it on a ring ? You can see by opening the consumer unit and see if there's a pair of wires on that fuse. While you're there see what size cable it is.
|
25-10-2012, 18:18 | #4 |
Senior Member
Join Date: Feb 2012
Location: Staffs
Vehicle: '02 Terrano TDI sport lwb
Posts: 3,787
|
Cable comes in one wire from consumer to double socket on wa, it's in truncking and it's 10mm so 53amp
|
25-10-2012, 18:38 | #5 |
Senior Member
Join Date: Apr 2008
Location: on the beach WEST WALES
Vehicle: Maverick TDi BLACK mmm
Posts: 15,136
|
|
25-10-2012, 22:56 | #6 |
Senior Member
Join Date: Nov 2009
Location: Norfolk, Poringland NR14
Vehicle: Terrano 3.0 SVE 2002
Posts: 1,549
|
MCB's are available in a number of surge ratings, generally type B C and D.
The vast majority of domestic installations use Type B. The .2 second ratings are: Type B: 3 to 5 x Rated Current Type C: 5 to 10 x Reated Current Type D: 10 to 14 x Rated Current Type D breakers are commonly used on large motor and welders. So ideally you need to change the MCB for a C or D type of the SAME current rating, as the MCB is sized to protect the wiring. |
25-10-2012, 17:51 | #7 | |
Senior Member
Join Date: Sep 2009
Location: somerset
Vehicle: terrano
Posts: 1,947
|
Quote:
|
|
25-10-2012, 18:16 | #8 |
Senior Member
Join Date: Mar 2006
Location: Central England, in the Heart of the Black Country
Vehicle: T2 2004 TDI SE LWB
Posts: 7,740
|
isn't the problem with welders that they are an inductive load an create a sudden surge when you first switch them on? not sure how to solve it, but I will watch with interest
|
|
|