View Full Version : Heating Woes


Banshee
24-11-2020, 10:32
Having some problems with our heating at home at the moment and due to my inherent nature of not trusting anyone else I'm determined to fix this myself as I refuse to believe it's anything difficult.

We live in 2 year old property with an Ideal Logic ESP 35 Combi Boiler in the kitchen, it provides all of the hot water from the taps and controlling the heating we have two Danfoss TP5000SI Thermostats one for the downstairs heating and another in the master bedroom for the upstairs heating.

We started getting an issue with one of the radiators not heating up in the study upstairs where the girlfriend is working from home at the moment so myself and my brother did a bleed of the system and turned all the heating on and shut the valves on the radiators downstairs which seemed to sort everything out for a week or so.

We have now lost ALL heating upstairs and following the same procedure as before suspecting it was the same issue, we bled all of the radiators again but this time with no effect. My brother was fairly confident that we had airlocked the system so we drained the system fully last night via the radiator closest to the boiler in the kitchen with a hose out the back door, we then opened up all of the bleed valves on each radiator, balanced the system and then re-filled the system and bled again. We weren't able to force any air out of the system at all and got a clear stream of water from every radiator and towel rail :nenau

The heating downstairs works fine and as soon as you manually flick the temp up past the ambient temp on the stat, you get the audible click from it and almost instantly, the boiler will kick into life and a few mins later, hot rads.

We do not get the same upstairs, we get the audible click from the stat again but the boiler just does not respond no matter how long we leave it on.

We're a little confused by this as now it appears that we have had two separate issues :nenau

I'm thinking that the stat must now be at fault as it isn't communicating with the boiler :nenau I've read that there is a wireless version of my stat which we def don't have, our appears to be the hard wired version.

I'm out of ideas and hoping you boys might be able to advise a few things that I may not have thought of yet.......

My plan of action this eve is to get home and swap the stats around thus proving if that is where the fault lies :nenau If that is the case I'll be a happy chappy as they are only £40 on Amazon

Please help!!! Her indoors is FREEZING

elty001
24-11-2020, 20:18
Not a clue mate but Dougie might be able to point you in the right direction :thumb2

Flying Torquewrench
25-11-2020, 16:04
Zac, first of all a disclaimer that I am not a heating engineer!!

We had a similar issue in a previous house. Turned out that one of the diverter valves failed. When we turned the thermostat up, you would hear the ‘click’ but because the valve didn’t run to its open position, it send no signal to the boiler to fire up.

Below is a link to a picture of a diverter valve.
https://www.amazon.co.uk/Honeywell-V4043H-Valve-Normally-Closed/dp/B001ANU6UA/ref=asc_df_B001ANU6UA/?tag=googshopuk-21&linkCode=df0&hvadid=231920353356&hvpos=&hvnetw=g&hvrand=15805084302202330009&hvpone=&hvptwo=&hvqmt=&hvdev=c&hvdvcmdl=&hvlocint=&hvlocphy=1006838&hvtargid=pla-421896607850&psc=1

There is a manual override on them. Move the little lever to the other side and see if the boiler fires up.

rayf3262
25-11-2020, 17:32
Generally you will find that the thermostat activates the zone valve and subsequently a micro switch in the zone valve actually switches the boiler on.

Banshee
26-11-2020, 01:13
Zac, first of all a disclaimer that I am not a heating engineer!!

We had a similar issue in a previous house. Turned out that one of the diverter valves failed. When we turned the thermostat up, you would hear the ‘click’ but because the valve didn’t run to its open position, it send no signal to the boiler to fire up.

Below is a link to a picture of a diverter valve.
https://www.amazon.co.uk/Honeywell-V4043H-Valve-Normally-Closed/dp/B001ANU6UA/ref=asc_df_B001ANU6UA/?tag=googshopuk-21&linkCode=df0&hvadid=231920353356&hvpos=&hvnetw=g&hvrand=15805084302202330009&hvpone=&hvptwo=&hvqmt=&hvdev=c&hvdvcmdl=&hvlocint=&hvlocphy=1006838&hvtargid=pla-421896607850&psc=1

There is a manual override on them. Move the little lever to the other side and see if the boiler fires up.

You nailed it mate well done although I'd already come to this conclusion after TDoug put me onto the trail last night. Turns out the Danfoss HSA2 actuator was broken for the upstairs diverter valve :doh

Took it off this evening and out of the system and opened it up in the garage and although there were 2 pieces of plastic broken off inside and when I tried to move it into manual the lever just flopped around :nenau

I've ordered a new one from Amazon and should be here on Saturday :thumb2

Generally you will find that the thermostat activates the zone valve and subsequently a micro switch in the zone valve actually switches the boiler on.

I turned the stat on in the bedroom upstairs only and had the valve open and it didn't fire the boiler up downstairs although I did get the click on the stat.

It appeared that the boiler only kicked in when the valve was opened so I presume it is the flow that turns the boiler on and operates the heating temp by regulating the flow of water??? I'm not sure :nenau

panelbeater
27-11-2020, 19:35
you need the pump to start befor the boiler will fire up.i know this because last friday my boiler did not come on,i bled all bleeders in system as it happened once when i had the new gas boiler fitted but next day would not fire up.all controls were asking for heat.i got the fitter out and it was air in system said that is commen.well as i said last friday no heating so called him out and it turned out that my pump was not working although all lights were on,he pulled live lead off then put back and pump came on,no charge to me but told me what to do if it happens again and pump needs to pump to start boiler.well it happened again thursday so pulled feed and repluged and all ok again but i will need a new pump fitted.mine has a computer in it which needs rebooting and they stopped making this pump as it proved a bad design.its only 8 years old but rather replace befor full failier.

panelbeater
27-11-2020, 19:39
bit off topic there as yours turned out to be a 2 way valve wich if only 2 years old is a poor show.but at least she will be warm.

Flying Torquewrench
30-11-2020, 22:19
Zac, did the new valve fix your issue?

Banshee
01-12-2020, 11:43
Zac, did the new valve fix your issue?

It did indeed :cool:

Actuator arrived on Saturday morn, I cut the electric and cut the cable down to size and reinstalled as per the old one.

Fired the boiler back up and dialled up the thermostat in the bedroom, went downstairs and the boiler kicked in as expected, back upstairs a few mins later and the radiators were all toasty hot again :splif

I've brought a bottle of 500ml Feronox F1 Inhibitor that I plan on adding to the system one night after work this week, apparently it's as easy and draining the towel rail down a little bit and pouring it in the top and running the system again then perform one last bleed

Thanks for the help guys :cool: